Using PVC conduit

Joined
May 13, 2021
Messages
2
Reaction score
0
Country
United States
Can sch 40 PVC be run along outside wall of a house or do I need sch 80. How many feet can be run before an expansion joint is required
 
Joined
May 15, 2021
Messages
397
Reaction score
47
Country
Canada
Yes, schedule 40 is fine. It's otherwise called rigid PVC. Distance before an expansion joint?....How long is your run?
 
Joined
May 13, 2021
Messages
2
Reaction score
0
Country
United States
Total run about 50 ft. Plan to run high under an overhang but along the way have tees down to outlets
 
Joined
May 15, 2021
Messages
397
Reaction score
47
Country
Canada
50 feet is not long enough to worry about intermediary expansion couplings. The assembly (as a whole 50' run) will expand on it's own as a whole length without buckling somewhere in the center of the run. Use the 2-hole PVC straps/clamps that are designed for the support of PVC, your fine. Use PVC cement, no need to worry about PVC cleaning solvent.....it's efficacy is questionable.
 
Joined
Nov 28, 2020
Messages
424
Reaction score
52
Country
United Kingdom
50 feet is not long enough to worry about intermediary expansion couplings. The assembly (as a whole 50' run) will expand on it's own as a whole length without buckling somewhere in the center of the run.
18 thou per degree F.

So 1¼" between 30° and 100°
 
Joined
May 15, 2021
Messages
397
Reaction score
47
Country
Canada
Those calculations are likely correct (18 thou per deg F), but on a 50foot run, the expansion can occur at the ends. If there was 200 feet of PVC conduit, the expansion that occurs in the center of the run (at approx 100ft) has nowhere to expand easily enough, and thus, buckle the center of the conduits overall entire run. It is an interesting figure you've commented on....I'll remember that, 18thou per deg F.
 
Joined
Nov 28, 2020
Messages
424
Reaction score
52
Country
United Kingdom
Those calculations are likely correct (18 thou per deg F), but on a 50foot run, the expansion can occur at the ends.
Only if it's constructed in a way which accomodates expansion and contraction.
 
Joined
May 15, 2021
Messages
397
Reaction score
47
Country
Canada
That's right, I agree with you. Each end of the run would have to have some room for movement, otherwise, I guess SleepyDog can just go-ahead and put an expansion joint in the middle for safety sakes.
 
Joined
Nov 28, 2020
Messages
424
Reaction score
52
Country
United Kingdom
I would. Or more than one.

Actually, I'd use steel conduit, not PVC, but that's another matter, and I accept that it's not as DIY-friendly....
 

Ask a Question

Want to reply to this thread or ask your own question?

You'll need to choose a username for the site, which only take a couple of moments. After that, you can post your question and our members will help you out.

Ask a Question

Members online

Forum statistics

Threads
128,916
Messages
1,266,497
Members
10,642
Latest member
ArcadePunk

Latest Threads

Top