Is this a ground cable coming into old panel?

Fee

Joined
Oct 27, 2020
Messages
10
Reaction score
0
Country
United States
I am doing a demo and renovation on a bathroom. I found a hidden panel behind tile and need to move it to the attic, which isn’t a problem. But in the panel there is this bare wire connecting to what looks like a grounding bar and the wire extends down through armored cable into the finished basement. There is a mix of NM and AC wire in emt conduit coming into the panel. What is this and does it impact me moving the wires to a new box in the attic?
 

Attachments

Joined
Dec 19, 2010
Messages
207
Reaction score
49
Bit late to the party

It's USA practice but best bet is disconnect one end at a time and check continuity.

All the metal parts should go back to a secure ground and that might be at the utility incomer, possibly an earth rod or the neutral if it's a PME system.

An installation tester and a long test lead would help.

Can't tell anything from the photos.

Take care.
 