1.5mm flex cable?

Joined
Oct 7, 2018
Messages
44
Reaction score
6
I have an electric inset fire that has the feed on the right side.
Would 1.5 cable be OK to change it to the left?
Cheers
Bob
 
Joined
Jun 29, 2020
Messages
21
Reaction score
5
Country
United Kingdom
I depends on how much current your fire needs. Some fires are just decorative - other have heating elements.

The current carrying capacity is stated below.
Source: www.cable-ratings.co.uk

It might be that your fire's output is stated as Watts rather than Amps. Watts = Amps x Volts, so for example, 14 Amps x 240 Volts (nominal UK Mains Voltage) = 3,360 Watts (3.36 KW), so 1.5mm it should be more than enough.

Hope that helps.

David.

CURRENT CARRYING CAPACITY (AMPS)
Conductor Cross Sectional AreaEnclosed in an insulated wallEnclosed in conduit on a wall or in trunking etc...
1.0mm²11A11.5A
1.5mm²14A15A
2.5mm²18.5A20A
 